hrmm i am not sure that is true, if you run 2 parallel circuits the voltage adds up the current stays the same, if you run 2 series circuits the current adds and the voltage stays the same. Sorry its been 20 years since i was in electronics school but i believe you are running 2 120v circuits in parallel when running 240, i could be wrong. Also i have never hired an electrician i do it all myself sorry for the ignorant statement ;-)
here is a site explaining it in more detail then you would ever want to know lol
You are correct in saying that it is basically 2 120v "hot legs" to make a 240v circuit, all ran back to a 2 pole breaker at the panel.
So, with that said, you are just dividing the amperage load between 2 hot legs instead of 1 when you run 240. That's why when you read the elec info on a ballast, it will say 9 amps at 120v, 4.5 at 240v. That doesn't mean that it only takes 4.5 amps to fire the bulb, it still takes 9 amps to fire it, but at 240, it is 4.5 amps with 2 legs totaling 9 amps to fire it up. Hope this makes sense. I'm pretty danked out.
No matter what, equipment needs so many amps to fire up. Lets use the ballast example again.
Run on 120, its 1 hot leg at 9 amps, at 240, it's 2 legs at 4.5 amps, at 3 phase, its 3 legs at 3 amps.
End of the day...your power meter will spin the same regardless of running equip at 120 or 240 or 3 phase for that mater.
The equipment will run a little more efficient, but negligible in regards to your power bill. The savings is gained when setting up the electrical system really only if you are going big. By this I mean it is cheaper to buy the wire needed to run big amperage load equipment then if you set it up for 120v only.