BuddyLuv said:I suggest beefing up the wire to 6 gauge. I was told by CAP that you want a 15-20% buffer for running this unit. I am running the same unit @ 50 amps @120v with 8 600w Lumatek ballast triggered to a CAP XGC-1 with no problems. CAP told me since my ballasts are 120v only to run 120, since the volts are cut in half the unit can now handle 80 amps at start up. I am only pulling 45.875. The six gauge wire will also fit in the MLC-8. And this all running off a single pole 50 amp breaker.
The mlc8 is rated 240v at 40amps. Upping the wire size would be dangerous.
8Gauge wire is rated for 40 amps.
The thing that everyone is overlooking is that on a 40 amp 220 breaker, there are two breakers in one, they should be connected by a tab. If one leg is tripping that means they are not connected. If the breaker tripps you should be resetting both breakers in unison. If one leg is blowing this obviosly isnt the right breaker.
Are you using 2 seperate 40 amp breakers, or one 40 amp double pole breaker?
Also the lights only consume 36amps, there shouldnt be any problem with start up.